s7-1200 hmi simulation

tulip

Member
Join Date
Oct 2005
Location
ist
Posts
236
We are using s7 professional v14 upd2.We open project run simulation prog.plc prog.is running test mode,we see.Hmi prog.is running (because we jump from screen to screen)but I/O field is shown ######.We could not understand.Thanks in advance for any help...
 
Make sure your PG/PC Interface is set correctly.

I was connected to a S7-1500 the other day and I could go online with the PLC, but when I started an HMI simulation I received the same issue with the I/O fields. After changing my PG/PC interface it worked fine.
 
No, it's in the control panel "Set the PG/PC Interface".

TO connect to the simulation, you need to choose PLCSIM 1200/1500.

To connect to a real PLC, you need to choose the appropriate Ethernet Adapter.
 

Similar Topics

...and I agree. Context: TIA Portal/HMI = KTP1200 (12" screen) In the attached redacted image, the values in the white boxes are entered by the...
Replies
10
Views
725
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
Replies
0
Views
164
I've got TIA portal v18, KTP1200 HMI. I want to add a slider bar (if that's the correct name for it) to an HMI screen. Baslcally, like a...
Replies
8
Views
1,142
See the attached pic ("workflow"). I want to create 2 workflows, depending on if the person who's just logged in is an OPERATOR or an ADMIN...
Replies
17
Views
2,487
Hello, I have a small application with a S7-1200 CPU 1212 and a KTP400 Basic HMI. When i am connected to the PLC with my PC i would like to...
Replies
1
Views
548
Back
Top Bottom