we supplied a system to a client with a panel contains s7-1200 CPU along with digital and analog I/O cards, it was commissioned and working fine.
they called us for a problem they had when i went there thinking it's just a bug in the code but we found the following:
1- the PLC is OFF power even i measured 23.8 vDC n it's terminals but for a period of time it powers ON
for 2 minutes then OFF again. also when i removed the 24 supply wire for some time and then connect it again, the PLC powers ON then after 2-3 minutes, again OFF.
i supplied the PLC directly to the power supply and the same result.
2- they added s7-200 PLC to the panel by their own and i noticed that they made a "jumper" from our
I/O cards to their own s7-200 cards which they installed as a back-up so that signals will be distributed on both cards ( i think it's wrong but i need confirmation from experts :) - s7-200 uses 220 AC )
so what could be the cause ? :cry:
I have never met such a practice.
Did you tried to disconnect their "jumpers"? Try to do this and see if the problem is returning.
if it were me, remove their gear and observe the result. If it works the problem is with their gear and they need to troubleshoot accordingly.
From an OEM point of view the warranty is now void.
You have either a short or severe voltage drop. I second Janner10's suggestion, remove every wire off the inputs and outputs and power up the unit then if all is well put back your own wiring only and walk away. Make sure to send them a huge bill for your time, this way they will call you first before making changes.
yes, it was as we expected in the replies, and the customer's team took the hit o_O and we are safe :cry:
thank you all (y)
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
58
34
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
98
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but...
242
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
43
2,957