PLC S7 1200 fail to go online

Kratos15

Member
Join Date
Sep 2023
Location
Ho Chi Minh
Posts
7
Hi. I’m trying to upload program from existing PLC S7-1200. Create new project in TIA v15.1 then upload. After upload successfully, go online but received some notice as “ online and offline difference” and Difference in lower-level component”. Please help to solve. Thanks
 

Attachments

  • IMG_2658.jpeg
    IMG_2658.jpeg
    156.9 KB · Views: 11
When I see this it is usually because the firmware version that you can set in TIA doesn't exactly match the firmware in the PLC. So long as the firmware in the PLC is in the same version ( 2,3 or 4) and has a higher number than TIA, then I haven't ever seen it cause a problem. They update PLC firmware more often than TIA software.
 
When I see this it is usually because the firmware version that you can set in TIA doesn't exactly match the firmware in the PLC. So long as the firmware in the PLC is in the same version ( 2,3 or 4) and has a higher number than TIA, then I haven't ever seen it cause a problem. They update PLC firmware more often than TIA software.
Thanks for your reply. I’m not familiar with Siemens PLC. Please advice how to set the firmware in TIA to match with PLC firmware?
 
To upload a running PLC project to PC (TIA Portal), you need:

1. Create a NEW PROJECT,

2. Then in PROJECT VIEW select:
Online->Upload device as new station (hardware and software)...

3. Select PLC and upload,

4. Go "online".
 
To upload a running PLC project to PC (TIA Portal), you need:

1. Create a NEW PROJECT,

2. Then in PROJECT VIEW select:
Online->Upload device as new station (hardware and software)...

3. Select PLC and upload,

4. Go "online".
I did same as your instruction and upload successfully but can’t go online.
 
Create a new project, add hardware, select s7-1200, then open that tree and select ‘unspecified s1200 CPU.
A yellow dialog box should pop up with ‘detect’ underlined, detect and it’ll upload the specific CPU hardware.

Then go online, and upload and it’ll bring the blocks up as well as the rest of the hardware.
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
82
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,878
Hello members, I have Siemens S7-1200 PLC (CPU 1214C AC/DC/Rly version 3.0) and I want to get backup from it. I know how the procedure works. I...
Replies
0
Views
139
Hi! Please share firmware for 6ES7212-1BE31-0XB0 https://support.industry.siemens.com/cs/nl/en/view/64789124
Replies
7
Views
748
Hi Folks. Has anyone used an SEW EI7C encoder with an S71200 PLC? If yes, how is it done? I use this same encoder in EI76 mode with a...
Replies
0
Views
260
Back
Top Bottom