S7-300 CPU, expansion rack IO modules crossed out in HWConfig?
jwilcoxson
Sep 2014
Georgia
31
Hello,
We have a system integrator at a site that is reporting that the IO modules in a S7 expansion rack (using IM360/360 modules) are crossed out, does anyone know what this means? The system is inoperative, and none of the DO module in the expansion rack have active outputs. It is a system that was previously working, and has had no changes until this.
Unfortunately, I don't have much more information right now, and the integrator will not be able to be back until tomorrow morning. At that time he is going to get me the diagnostic buffer and we will troubleshoot more.
I assume this was in the online view of the HW Config. Usually crossed out means that the module couldn't be reached.
Could mean anything from the module missing, to the connection cable being unplugged, the device not powered on, etc. I've never worked specifically with the expansion racks before, however, we always just use distributed IO.
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
144
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
188
Hi there, I have an application where I’m required to connect Siemens S7-300 PLC (Profinet) to Allen Bradley Control Logix Remote I/O Rack &...
3,692
i have 314 siemens cpu the machine stopped and all plc output modules doesn't give any output . i checked it and all modules are ok. when i...
3,307
Hello guys, Our working machine CPU I am trying to add one logic but when I am click download then warning ⚠️ message coming that Unable to...
1,410