S7-314 cpu and SM332 I/o error
akrogh24
Mar 2014
Bramming
I have a problem with an analog output sm332, it says "I / O access error or parameter assignment error" the error came after I moved modules from the Rack 0 to Rack 1, IM365 sitting in slot 3, and SM332 sitting beside in slot 4
under the tap "Diagnostis interrupt" is there a messeage: Parameters have not been assigned to the module.
they are all 0-10v (E)
I changed PQW 363-374 to 384-391 in the program, but the error is still there, does anyone know what to doo.
Allan Krogh
if i look in the hw config it got new adresses (PQW 363-374 is change to 384-391)
i have a picture off the hw config but i dont know how to upload it here?
Hej Allan.
It is not clear to me what you have done. You write you moved modules IM365 and SM322 from rack 0 to rack 1.
The two IM365 modules makes the connection between the racks, so I guess that IM365 was not moved, or what ?
Did the SM322 card sit in slot 11 in rack 0 ?
Post a screenshot of the HW configuration before the change.
Try to go back to the previous situation before you added the CP343-1 LEAN card.
Remove the CP343-1 LEAN and move the SM322 back to rack 0, and load the old program. If the problem does not clear it seems that the SM322 is defective.
sm332 analog output moved from rack 0 slot 11 to rack 1 slot4, im365 did not move
cp343-2 was inserted in rack 1 slot 11
Maybe this can help:
Module Information - CPU 314 "Diagnostic Buffer" Tab
Event 1 of 10: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 384
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
08:22:50.122 AM 05/07/2011
Event 2 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.113 AM 05/07/2011
Event 3 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.106 AM 05/07/2011
Event 4 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.098 AM 05/07/2011
Event 5 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.089 AM 05/07/2011
Event 6 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.082 AM 05/07/2011
Event 7 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.064 AM 05/07/2011
Event 8 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.056 AM 05/07/2011
Event 9 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.049 AM 05/07/2011
Event 10 of 10: Event ID 16# 2942
Priority class: 1
08:22:50.040 AM 05/07/2011
All it says is that the CPU cannot access the address PIW384 of the analog card.
Try what I suggested before:
Can you post your project here? Would be easier to check out that way..
Hello to All, Recently I install a CP343-1 Lean to communicate with a CPU 314 IFM, however I can't go online when I'm connected via CP343-1 Lean...
1,672
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
1,944
Hello Everyone! As the title suggests, i would like to know how to program a "First Scan Bit" in S7-300 PLC CPU314. I made a sequence with 3...
3,164
Hello all, I have to solve how to repair a damaged CPU314PNDP by 230VAC, which came to 24VDC power supply line. Does anybody know, which...
2,580
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
2,408