s7 314 CPU replace by s7 315 CPU
dwcy
Oct 2004
Hong Kong
22
There is a system which is use S7-314 (6ES7 314-1AF10-0AB0) as the CPU. My problem is that the the working memory of the CPU (48kB) is full. But I need to add more program. So, I want to change the existing S7-314 (6ES7 314-1AF10-0AB0) to CPU 315-2 DP (6ES7 315-2AG10-0AB0) which working memory is 128kB.
I want to know when I change the CPU, how many thing do I need to modify the existing program? Such as the hardware config, network config, etc..
Dennis
Hello Dennis;
If the CPU is all you want to change in your project, then you can do it easily in Harware config.
For security purposes (and your peace of mind) start by creating a duplicate or an archive of the existing project; less hair-pulling if something does nott go quite right...
Open the HardwareConfig editor of your working project. Just drag the new CPU model (from the hardware catalog) over the CPU314 in Rack 0, slot 2. There is a setting in the Options menu that allows you to swap modules. If all goes right, you will be asked if you want to transfer the existing program to the new CPU (of course you do!). Just make sure to check the MPI and Profibus addresses of the new CPU, and specific CPU properties, suc as Clock byte and memory retention (this is not transfered); all other information from existing modules and networks should be retained.
Hope this helps,
Daniel Chartier
Hello to All, Recently I install a CP343-1 Lean to communicate with a CPU 314 IFM, however I can't go online when I'm connected via CP343-1 Lean...
1,675
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
1,947
Hello Everyone! As the title suggests, i would like to know how to program a "First Scan Bit" in S7-300 PLC CPU314. I made a sequence with 3...
3,170
Hello all, I have to solve how to repair a damaged CPU314PNDP by 230VAC, which came to 24VDC power supply line. Does anybody know, which...
2,583
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
2,410