Dear Expert
i have an system in which i am using cpu 315 2dp.
now i have to exchange data between 3 nutrunners(with mitsubishi plc ) which have ethernet port.so i am thinking to add cp343-1 with s7-315 2dp
1. how to add gsd file of mistubishi plc in s7 hardware on profinet.
2. which communiction blocks should i use?
or should i use any other cp for this application please suggest.:mad::mad:
What about standard TCP connection? Its easy to handle inside the S7 (NetPro connection and blocks FC5/6 from the CP-library) and the Mitsubishi should be able to do the same. No gsd-files required.
ys they are going to give me profinet gsd file
but i can see a profinet network in siemens hardware after i add cp 343-1 to connect mistubishi plc
In STEP7, open the HW Config, then in the HW Configurator select from the menu "Options" ... "Install GSD file".
When the GSD file has been imported, you can find it in the HW Catalog under "PROFINET IO" ... "Additional Field Devices". From there, copy it to the Profinet bus that is connected to the CP343-1.
In the STEP7 program you have to add the blocks PNIO_SEND and PNIO_RECV to exchange data via profinet.
thanks mr. jasper
but i am not getting profinet bus with cp 343-1 in hardware.
how should i get this bus please tell me for cp 343-1
You are being inconsistent.
You need a CP like the 6GK7343-1EX30-0XE0.
In the HW Configurator, select the PN port on the CP. Then from the menu select "Insert" ... "PROFINET IO System".
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
71
Hi guys! Anyone here who has done modbus TCP communication straight up with AG_SEND and AG_RCV? Any snags one should know about? I've done some...
2,078
Dear Sirs, I had a problem with CP 343-1 with CPU315-2DP.I had newly add the CP343-1 Ethernet module to the hardware to allow me to access this...
2,639
I am trying to get data from a Serial Barcode scanner from a Siemens S7-300 CPU 315-2DP . I am using CP343-1 ethernet Interface Card and a MOXA...
2,970
Have a strange fault issue. New system ran for 3 days then cpu faulted out with vague error messages. Rack make up is. 315-2DP IM360 343-1 341...
4,825