S7 Profibus DP Device limit
32 bus attachments max in a segment (a segment being the cabling between a pair of terminating resistors), total cable length in the segment will depend on your bus speed.
If you use MPI/DP interface as DP Master there is a limit of 32 slaves, on integrated DP interface you can connect 124 slave stations.
Gregory .... did you read the original post carefully? ......
tmccoin said:
......without using repeaters?