S7 System
mcnaughtc
Feb 2007
Vanderbijlpark
Good day all
I'm currently putting together a new control system consisting of a PCS7 control system 4 x Siemens 416-3 Cpu's and multiple remote ET200M I/O Systems
Most of the remote I/O Stations are linked via fiber optic/OLM Modules as they are mounted out in the field.
And in the cases were there is a short run of 50 meters or less I have stuck with standard profibus cable run well clear of any power lines, and these runs are all housed inside buildings.
Am also running 2 x redundant servers, 1 x Client and 1 x engineering system connected via industrial ethernet to fiber optic to a remote building where the PLC'S are housed.
I've attached 2 simple drawings of layouts of the system for a rough idea of the layout.
So in short i'm putting this out to get any ideas/comments on the system, where improvements could be made or things done differently. So that I could incorporate it into the current system, budget permitting of course.
Cheers
Craig
Hello mcnaughtc;
Well, at first glance, the layout appears workable; it would require a lot more details before we could give an informed criticism of your project.
Your selection of the different OLMs has of course taken into account the type of fiber and the number of optical interfaces required at each node. The electrical star and bus topologies that you show are supported without problems. Distances are only limited by the type of fiber, so this should already have been taken into accopunt; speed is independant of distance over fiber.
The latest version of OLMs include some diagnostic features that you will be able to use during commissioning, so that should be useful.
Hope this helps,
Daniel Chartier
Daniel Thanks for the Reply, and comments
What sort of other details would you like? am sure i can provide them.
What sort of diagnostics options are you refering to for the OLMS?
Cheers
Craig
Hello Craig;
here is how Siemens" update FAQ descibe the diagnostic functions of the OLMs:
Enhanced diagnostic features and fast fault localization by signaling of the FOC line quality via LEDs and measuring terminal (enables reading the signal level of the FOC line quality via an analog module into a PLC)
</SPAN>
Specifically, there are CHANxLevel LEDs that indicate whether the quality of the optical signal on a specific interface are of acceptable levels; and the installation/operation manual shows how to connect a voltmeter to a specific point to measure to "optical level" voltage. This will indicate fiber wear or tear. It can be linked to an analog inoput and read by the PLC if required.
Hope this helps,
Daniel Chartier
Hello, I have no training in maintaining potable water systems, so forgive me if some of my terminology is far off the mark or if I'm focusing on...
99
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
108
Hi all, This is going to be a long post apologies. I'm also a complete beginner to the world of PLCs. I'm currently working on my first ever...
476
Hello everyone, I'm working on a project that involves controlling an array of nozzles within a CNC environment, where the nozzles travel along a...
191
I am utilizing both HMI and SCADA for my project. Both HMI and SCADA have identical tags. When I modify the tag value on HMI, it is reflected in...
165