I want to convert from S5 to S7 Plc.One of them is S5-115U Cpu941B and the other is S5-115U Cpu943B .All of them have 64 kB Eprom ,digital inputs and digital outputs also..Which type S7-300 Plc can I use for this project?Second question:A lot of SB Blocks are used in S5-115U Cpu 943B.Which program do I need for opening these blocks?and is convert possible?thanks in advance....
 
941B is a very weak CPU.
943B is a bit better, but a factor 100 slower than todays CPUs.
Any current S7 CPU will have enough power and memory to run the same programs as the old S5 CPUs.
The decision to what S7-300 CPU to chose should be based on how much i/o and what communication there should be. Be smart and chose a CPU with ethernet on-board.
Unless you want to cut costs to the extreme, I recommend that you chose a 315-2PN/DP as the minimum.
 
Thanks for your replies,S5-115U Cpu 943B has got 224 DI,96 DQ and OP393-III.Other cpu 941B has got 64 DI,32 DQ and OP393-III.
I want to reduce costs as possible.
 
Go for a 315-2PN/DP.

If very low cost is required, consider IM151-8 with ET200S i/o.
For the CPU943B you may have to split the i/o into several "racks" via Profinet. It is not difficult to do.
 

Similar Topics

Dear Members; We are going to design a Simplex Control System With Following: 1. 24 Digital Inputs (SIL 2) 2. 24 Digital Outputs (SIL 2) 3. 4...
Replies
14
Views
1,152
Hello, Not able to find Modicon DO modules BMXDDO3202 in EcoStructure Control expert V15 catalogue. But i can find only MBXDDO3202K. Can you...
Replies
2
Views
510
Good morning all, We want to build a test panel with IO link to get familiar with the product line. We have ML100's and SLC 5/03's currently...
Replies
12
Views
1,633
Hi,I need to build a PLC panel with a CUP & I/O cards, the panel to be communicated with a remote (500 meter away) extension module station. I...
Replies
9
Views
2,585
Hi All, EDS file is available for the device profile with the following assembly instances and max size (based on parameters in the respective...
Replies
0
Views
3,004
Back
Top Bottom