Sensor for reading water in steam environment
... the sensor when not placed over the tube gives stable readings. the only thing we can figure out is that the steam in the tube being seen as the water level. as it goes to the top of the tube, the sensor no longer sees the steam.
by "steam," do you mean small, visible, liquid water droplets above the water level i.e. i.e. the water/vapor interface?
by "it," do you mean the water level?
by "no longer sees the steam," do you mean the sensor gives reasonable values?
Guided wave would be my recommendation as well. Vega has some great sensors, even ones where you can cut the probe to length as required.
[..] heated to 200 degrees F.
So not boiling, but still higher than what most electronic sensors are rated for.
we have been using a turck rod sensor with a magnetic float which has now gone bad after only a few months [..]
Was this rated for high temperature ? If not, that would my suggestion.
this is not a pressurized vessel.
Then instead of the float you can measure pressure. There are sensors that are intended for being dropped into a tank and report the level based on the pressure. Here is a high-temperature one:
https://www.ato.com/high-temperature-level-sensor-20m
Eureka
I suspect guided wave is the long-term non-contact solution, but I wonder if hose spraying water slowly on the outside of the level tube will allow the ultrasonic to yield good values again.
There will be a small difference (~3% max, so up to maybe half an inch over 18") in the level between the tank and the tube, which has probably always been true to a smaller degree* but unnoticed.
* smaller temperature difference
Only good to 212 deg F. I'd be leery. Also, how contaminated does this water get? You're dipping a product, is there any particulate that is left behind? These guided radar type in a closed diameter of 1 1/2" may have issues over time with buildup and if the dielectric of the solution is changing.
drbitboy,
when i refer to steam, i mean the vapor coming off the water, like what you see
on the highway after a quick shower.
by it, i mean the vapor going up the tube. again, like the steam you see on the highway after a quick shower.
when the steam dissipates, the sensor gives stable and accurate readings.
james
drbitboy,
james
Okay, so wet steam or aerosol. So you, and presumably the ultrasonic sensor, are seeing the liquid water droplets.
Dry steam as a vapor is transparent to visible light.
Try the hose; if you can cool the water in the tube, the droplets should dissipate and the ultrasonic might work again.
What we have used on our CIP tanks (caustic)are the endress & Hauser hydrostatic (pressure sensors), these would need to be in the bottom of the tank though, they certainly work at 90 Deg C without problems ours were calibrated in litres & went from 0-4000 litres, there is an area (very small) at the bottom of the tank due to the convex shape with bottom exit valve so mounted about 3" up on the domed bottom.
We converted some other CIP tanks from high/low level rod sensors to the above ones just required a mounting boss cut & welded to the bottom of the tank (we actually used an inserted threaded flange) so the diaphram sat above the bottom of the tank due to the possibility of some accumulation of product may occur at the bottom being a flat bottom tank.
Hello Ken Roach, Thank you for your quick reply , As informed earlier i want to read P&F Sensor data on Micrologic 1400 series B using MSG...
17
5,848
Have you seen a PT100 sensor reading going slowly up, even after heating power turned off ?! and it keeps rising for several minutes ... It looks...
4,545
Hello everyone, I have a pretty basic question which I can't seem to find any information for. I have an ultrasonic sensor connected to my analog...
3,506
Hello all, Let's say that we have a plant where there's no PLC or HMI, and we have a temperature sensor with a 4-20mA transmitter. If I want to...
2,817
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
23
598