Siemens 1200 flash and firmware
geniusintraining
Jun 2005
SC
8,280
I have a customer that has a failed 1200, they are getting a replacement from me its a 6ES7212-1AE40-0XB0, his original has FS02 and the new one is a FS04 firmware, they do not have any software they only have the program on a MMC running in the PLC
18 months ago they had a failure and swapped the PLC and also the MMC and its ran great but it was a FS02 swap to a FS02
So my question is can they take the MMC and install it in the new PLC with the two different firmwares ?
Yes. In theory, if the part number is the same, and the FW on the new module is same or higher than the old module, you should be able to move the SD card no problem.
I've never been 100% clear on what the FS numbers mean, but it definitely isn't the major firmware rev. The part number you listed doesn't support firmware below V4 (newest is v4.2) It's possible it represents minor firmware updates, but I think it just means manufacturing changes that don't require a full part number change.
In my experience, Siemens projects tend to be pretty portable to newer models. Siemens very rarely breaks compatibility with old FW versions. Upgrading from V3 to V4 in the 1200's was a mess (part number, portal version, and FW all had to change together), but besides that Siemens PLCs have been pretty flexible for spare part compatibility. They will almost always pretend to be older FW revs or prior part numbers, and sometimes similar part numbers as well. I wouldn't be all that surprised if you could take that 1212 project and swap it into a 1214.
Not sure if you know... but reading further am I correct in that the 40 in the part number is the major firmware, trying to decipher their part numbers
6ES7212-1AE40-0XB0
Group (PLC) = 6ES7
Family=212
Power and I/O = 1AE
Firmware = 40
Group (PLC) = 0XB0
:confused:
Mark
From TIA Portal 13
6ES7 212-1AD30-0XB0 is firmware 2.2
6ES7 212-1AE31-0XB0 is firmware 3.0
6ES7 212-1AE40-0XB0 is firmware 4.1
From TIA Portal 14
6ES7 212-1AE40-0XB0 is firmware 4.2
I stopped trying to figure their parts reference logic many years ago, it probably makes perfect sense in German. Although the S7-1200 seems to be more multicultural so that probably gets even more confusing. Expansion units for the S7-200 used to end in 0XA0, but the PLCs were 0XB0. The SIRPLUS versions end in 4XB0. I know that on a cold day I like a nice hot drink of OXO.
Maybe I will join you 🍺
A couple other vendors I can just make up a part number with what I need and see if its a real part
Phoenix Contact is another one o_O
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
271
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
144
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
189
Hi Experts, I would like to make firmware upgrade from v3.0 to v4.5 (S7-1200 CPU 1215C). Can I do it from v3.0 to v4.5? Do I need to take some...
312
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
43
2,935