jitendrakpatil Member J Join Date Aug 2005 Location mundra Posts 8 Sep 27, 2006 #1 What are the possible causes for fault "F039" (Precharging Ground Fault).
Ken M Member K Join Date Mar 2004 Location . Posts 1,136 Sep 28, 2006 #2 Wild guess - does "AFE" refer to Active Front End? I've heard that term used in connection with some drives but never used them myself. Might this post be better on a drives forum than a PLC forum? (and sorry, no, I don't know of one). Ken
Wild guess - does "AFE" refer to Active Front End? I've heard that term used in connection with some drives but never used them myself. Might this post be better on a drives forum than a PLC forum? (and sorry, no, I don't know of one). Ken
PLucas Member Join Date Apr 2002 Location Gillingham Kent Posts 1,742 Sep 28, 2006 #3 Ken M said: Wild guess - does "AFE" refer to Active Front End? Click to expand... Excellent wild guess Ken! We have 4 AFE's in service here, but, guess what, I can find my manuals for them! I believe that F039 means that the AFE has detected an earth fault on the DC bus, I would check the DC bus for an earth fault. If you can find no problems with the DC bus it might be the case that the IGBT's are on their way out, how old is this AFE? Paul
Ken M said: Wild guess - does "AFE" refer to Active Front End? Click to expand... Excellent wild guess Ken! We have 4 AFE's in service here, but, guess what, I can find my manuals for them! I believe that F039 means that the AFE has detected an earth fault on the DC bus, I would check the DC bus for an earth fault. If you can find no problems with the DC bus it might be the case that the IGBT's are on their way out, how old is this AFE? Paul
DickDV Member D Join Date May 2002 Location Kalamazoo MI Posts 2,324 Sep 28, 2006 #4 Check your incoming power for balance with respect to ground. Ground and Ground Fault detection can be troublesome when your power is floating or the three phase supply is running with one leg grounded.
Check your incoming power for balance with respect to ground. Ground and Ground Fault detection can be troublesome when your power is floating or the three phase supply is running with one leg grounded.
Leadfoot Member L Join Date May 2005 Location Red Stick, Cajun Land Posts 577 Sep 28, 2006 #5 I have found grounded motor leads causing Ground Fault trips on some drives too.