Hello,
I am having a problem with a Siemens mp370 HMI.
It runs well until the machine is down for a hour, or the power is switched off, then all the set points we've set in the machine are lost and have to be put in again.
for example there is an encoder and the machine rotation is measured 0 - 360 degrees.
I want a valve to turn on at 100 to 180 degrees. After a power off this will be lost and the data will have to be put in again.
If we power the machine OFF all the set points are lost.
Is there a setting to retain the set points? Am i losing the Encoder data and this is effecting the set points?
any ideas?
Hmm
Isn't this problem on the PLC side ?? All data you give, is this data stored in DB's ? What CPU is connected ?, if it's a recent one, then all DB's are retentive, then only the program can be responsable.
Hello,
any ideas?
1. The Data input is sent to MD's. These are read by the PLC.
The input is from the MPI. The PLC does not write these to the HMI.
If is all goes wrong I'll input the data to the PLC in the PLC using move instruction......This will mean that the data cannot be adjusted from the HMI which rather defeats the purpose.
2. The PLC is a S7 300 317-2EK13-OABO
Hi
I think the MD's are not in a retentive area. You can make them retentive in de Hardware Configuration, or you change the program. DB's allways retentive the M area depends on what's made retentive in the Hardware.
In the other machines, we dont have this problem.....
I have looked and there are different hardware configs for retentive memory.
looks like this is the problem.
thanks
Need to put in a new touchscreen digitizer. Does anyone know the procedure or how difficult this might be? Have never taken one apart, so I don't...
1,412
Buona sera, Ho dei problemi nell' interfacciare PLC S5 con HMI 2a Gen. Siemens (ad esempio KTP400) tramite IBH Link S5++. il mio obbiettivo è solo...
100
Hello colleagues, On a Siemens Multi panel (MP 377 12") of a machine (S7-300) at a customer's site, some parameters need to be changed that have...
312
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,451
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
164