Siemens LOGO! 8 Ethernet Comms
aiki202
Aug 2007
Pennsylvania
178
Regarding a Siemens LOGO! 12/24RCE 6ED1052-1MD00-0BA8 controller...
- What comms protocols does the Ethernet port support?
- Is the port protocol select-able (SIMATIC S7 protocol or Modbus TCP/IP, etc.)?
- Internet search results and the manual are confusing.
You get them both.
I have used several of these and you can use both the S7 protocol and the Modbus TCP/IP protocol. You can even use both at the same time. (We have only used the S7 protocol to connect with a Siemens HMI)
All the standard I/O External and Internal are premapped both to S7 and Modbus registers. The variables you program can be mapped to a fixed range or S7 tags which also defines what Modbus registers they are mapped to.
I would guess that you could connect to multiple Modbus or S7 devices. It can be connected to like 8 other devices.
Good luck
Hi all, First, thank you for reading the thread. So I had a task as the following: An up-counter must be programmed as part of a batch-counting...
293
Hi Lads, I want to implement a flood prevention system with my domestic water pump. The intention is to have the water pump cut off on a daily...
1,079
We need a Really Simple and Cheap controller that has a display or a Web Interface where we can change some set points. We were thinking about a...
1,047
hello i have LOGO! 12/24RCE and i am looking for a schematics of electronic board. Or if someone know what is the burned component on the photo.
1,412
Hi, I'm no expert in PID regulating so I need some advise. I have a VFD controlled deepwaterpump that is maintaining the pressure in a closed...
24
11,914