Siemens MP Terminal date/time field
cjd1965
Apr 2007
UK
1,659
Hi
Basically I have a date/time field set to TIME only and using an internal DATE_TIME tag
On power up the date/time field shows ####### which I expect because it has no value. If I enter 00:00:00 the data is not accepted
If I then add a second date/time field as DATE and TIME with the same tag, and restart the runtime, I can enter a value 00:00:00 and the display shows DD/MM/YYYY 00:00:00
The original display also shows 00:00:00 and can be edited as normal
Anyone else had this?
I created a new page where the customer had to enter the data in new date/time boxes but they are a pain.
Siemens Technical have passed this back to Germany
Hi
Is it WinCCflexible or tia?
The HMI shall never display ####### it should display the set start value (base value) of the tag upon restart.
What happens if you change the base value of the tag offline?
attachment.php
In simulation mode simulating an mp277 the field displays my set base value when the simulation restarts.
Hi Bratt
If I open it in PC runtime it works fine, it is only when on the panel. I think you gave me the answer because the base values are empty I get the #####
I think my answer is to use base values but this does not explain why I cannot enter a time value
I am using WinCC Flexible 2008 SP3
Hi Guys, Hoping we still have some Siemens Old hardware Gurus on here. We are trying to support one of our long time customers. Who have obtained...
967
What is the difference between Siemens terminal block 6ES7193-6BP40-0BA1 and 6ES7193-6BP40-0DA1? Can they be used interchanged for an analog...
1,244
Hello, I am troubleshooting a fault on a Terminal assignment for F-DI 8×24VDC HF. Terminal 15 says its a; VSn: Internal sensor supply, channel n...
2,449
Hi guys, Any of you guys know if using ET200S, do I still need to put terminal block (Wago/Pheonix Contact)? Can I wire the field signal cable...
2,768
I'm using the Siemens PRONETA software to do some IO testing currently. I love the simplicity and fast testing capability. Does anyone know about...
67