Siemens MP277 connection with multiple PLC

Werner

Member
Join Date
Apr 2005
Location
IJsselstein
Posts
336
I want to connect 2 plc's (in the same Siemens S7 project) to one HMI (siemens MP277). I am using WinCC flexible. I have done this in the past without any problems.

But now WinCC flexible reports an error. (The HMI address is not unique). This message is correct because I have defined two connection lines. One from HMI to plc 1 and one from the same HMI to plc 2.

If a make this setup in a mobile panel it works without problems...

Anybody an idea on how to solve this?
 
I solved the problem. I disconnected all displays from the network in netpro. One by one I connected them again. (Checking all settings while conencting them again) At first all settings in netpro looked ok. But the displays had double addresses! (Strange because netpro did not report any errors upon compile).
 

Similar Topics

Hello, I have a need for a script to read a text file from a shared folder on a remote Windows XP PC. I can do this locally using an ethernet...
Replies
0
Views
3,824
Good day, May I ask, what do I need to perform MIGRATION of HMI program from Siemens MP277 10" Touch hmi to TP1200. I already have WinCC Flexible...
Replies
0
Views
173
Hi All, I currently have an damaged MP277-8" Touch panel (6AV6 643-OCB01-1AX1) which I am able to backup (.psb) via ProSave. We are in the...
Replies
1
Views
2,871
I need some clarification about uploading the HMI file from a Siemens MP277 to edit it in WinCC. Although the machine manufacturer is no longer in...
Replies
1
Views
1,366
First off, I am not a Siemens guy. I am trying to help a customer who bought an older machine with Siemens equipment in it. So far I have had no...
Replies
8
Views
3,658
Back
Top Bottom