Siemens S5 Block problem
RoTaTech
May 2003
Cobourg, ON, Canada
418
Good morning All
I am just doing my first S5 job, (lots of AB and Omron experience).
We have a working machine; the parent company sent over a program from an (almost) identical machine for me to load.
I uploaded and saved current version (OB001 and PB001-003), and loaded new version. Machine does not work now. Yes, it is in RUN mode, and I tried the load both without STOPping the PLC, and after STOPping it. Yes, the addresses are identical.
One (small, I think) difference is that there are PB001-006 in the new version.
First thing that should happen is:
In PB003 - Push Start PB, conveyors come on. The original program used a self-seal rung, the new one uses a Latch/Unlatch - I know they should work identically. No, the Unlatch condition is not active - I even put a dummy bit in there to ensure that.
I can see the logic flow while monitoring, my Start PB is running to the Latch output, but the (real) output does not come on nor does the (L) stay lit when I release the PB. Again, the (U) rung is not being triggered.
If I load the original program back in, the machine works. Ergo, I am doing the transfer and RUN/STOP correctly.
I even tried modifying that PB, in the new program, to only contain -||- pushbutton -(motor); this does not work either!
Any ideas? Please?
Please check the program to see if the "latch" or "unlatch" are used in more than one place?
Can you post a copy of your project here?
A few weeks ago I had to reset the PLC then do a download.... not sure why but it was acking something like yours... the output would be true but it would never turn on
I have posted a procedure on the rest of S5's before if you don't know how, what is you exact part number? as I have some good manuals that may help (if they are for the correct one)
EDIT: Post both programs... I have a compare program and I will see if there are any hidden bits that you are not seening
The L and U bits are not used elsewhere. That is usually my first check.
I just had a closer look at the OB01 file, it has a conditional jump to the PB where our outputs are; the old program had unconditional. I am going to try reloading and short out/remove the conditional.
Dear Experts, I wanted to discuss a problem which I am going through now and you experts can suggest me a solution for this. I am using S120...
1,638
Hi, I'm trying to transfer all the blocks from a Siemens S5-115U CPU943 using Step5 programming software. The S5 is online and also it is...
11,559
In a data block, if the tag is ticked in the "Retain" column", is it meant to be retained after cycling the power to the PLC? I'm finding that...
752
I'm having a bad day. Daft question coming up...Anyone know why I can't add anything into this DB? Add button is greyed-out. Thanks
1,629
Hello, We have a startup valve, that has to open on startup etc. We also want to know the flowrate throughe valve. They told me that in previous...
17
2,776