We are replacing an existing FM 350-1 module in an existing installation. If it's a one- for- one swap, do we need to change or update anything in the hardware configuration? Do we need to go online and navigate to the module to set any parameters? I've fone this before but it's been about 10 years lol. Thank you!
 
Short answer - no... as long as it's a FM350-1 module you're replacing it with. Generally even if the newer module has a different part#, it can just be installed in place of the old one with no configuration changes.

Just for confirmation, what is the old part# and the new part# of the FM 350-1?
 
Also, when putting the front screw terminal on the replacement S7-300 module, you have to remove the white circular "tabs" that are on it. Otherwise the screw terminal will not plug all the way down onto the module. Hence the "No auxiliary voltage" error.

But, still, you cannot put a SM 338 POS module in place of an FM 350-1 module.
 

Similar Topics

Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
263
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
142
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
Replies
1
Views
187
Hi Experts, I would like to make firmware upgrade from v3.0 to v4.5 (S7-1200 CPU 1215C). Can I do it from v3.0 to v4.5? Do I need to take some...
Replies
6
Views
301
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,907
Back
Top Bottom