Siemens S7-200 no way to connect?
Leukic
Oct 2018
Leesville
93
Had an issue with the machine cutting stopping in the middle of auto running. So I go to the cabinet to plug up to the plc and well both of the connections for the ppi cable are being used.
1-Goes to the HMI
2-goes to the 2 drives for the belts.
Can I just disconnect the cable going to the hmi while the machine is running to observe a fault? Or will this cause the machine to stop?
No, odds are it will stop and fault out.
Is there a place to plug in? SOME (not all) will let you piggyback onto the connection, check the HMI and drives also and you will need a multi master cable for this.
I don't see any place to piggy back and I have the cable.. Unless the back covers of the profibus cable come off. Which I can check here shortly.
Call your local rep and buy a Profibus connector that allows you to hook up your cable.
I think you can also get the Profibus connectors from other vendors.
Wago, Siemens and a bunch more.
I would suggest changing one of your Profibus connectors for the newer style- then you can piggyback off the network and go online using a CP5511/ CP5512 card.
Regards
Daniel
Thanks, Rob Collinsd70 and bkottaras. I will give my local siemens rep a call. He was the one that supplied me with USB/PPI Multi-master cable.
Profibus DP Connector: 6ES7 972-0BA50-0XA0
C79459-A1890-A1 is the Part Number for the CP5511/CP5512 Cards, in brief; CP5511 is suited for 32 bit systems <=Win2k. CP5512 is confirmed working for <=Windows XP- the converter provided allows you to connected to a DP Master as a secondary DP Master (normally on the reserved DP Address 127).
Alternatively you already have Serial/ USB to PPI- so just change the connector and you should be able to connect this way.
Regards
Daniel
Hi Complete newcomer to S7 so go easy on me... Siemens S7: What cable do I need to connect S7-1200 PLC to HMI? The touch screen is one of these...
2,611
Hello, I am very new to Siemens but have been doing AB for many years. I don't have the information I probably need but here's the story. I have...
1,147
Hello; i'm having some troubles with a com test i'm handling. i have another end for it, but for now i would like to have : M241 in io_scanning...
3,487
Dear experts, I can't connect to Siemens s7 200, I have Siemens ppi cable but I don't have serial port on my pc so I used serial to usb converter...
4,544
Hey everyone, I have a Siemens PLC s7-200 that I wanted to connect to in order to upload the program from it as a back up for me. The PLC I have...
19
7,173