Siemens Step 7 SFB 4 "TON"

vanilla05

Member
Join Date
Jul 2008
Location
Singapore
Posts
8
Dear all,

i tried to use the SFB 4 timer but it seems that the timer just refused to count and im not sure why.

I understand that with an IN and time at PT, the output bit will be activated when PT finish timing. But what happen was that the output bit becomes 1 as soon as the IN becomes 1.

Basically, there isn't any delay.

Will anyone kindly attached a print screen on the variables and Db linked to SFB 4?
 
Hi alan and L D[AR2,P#0.0],

thanks for your prompt reply. the problem indeed lies in the simulator. The problem is solved as soon as i installed the patch. Thank you once again.
 