Hello, dear experts. We have problems with the following mature Siemens UPS (issued in 1993):
Data from enclosure label:
SIEMENS UPS B4208 / 16 puls rect.
TYPE: D400/115
Order No: 6SU4208-0AA00-1MA0
P = 80 KVA.
After switching off the UPS for battery maintenance the inverter doesn’t work. After switch on rectifier input switch-disconnector Q10 the red LED H4 lights up on the module A101 (see page 1 in the Attachement). After pressing the button Inverter On/Off and button Enter (Invertor On) a red error symbol lights up on the display. This error could be reset by the button S1 on the module A102. Simultaneously red LED H4 lights on the module A101 (see page 3 in the Attachement).
When we try to start the inverter again, red symbol of inverter’s error turns back on the display. After error reset (by the button S1 on module A102) red LEDs H1, H2, H3, H5, H6 light up on the module A101 instead of LED H4 (see page 2 in the Attachement).
When we try to switch on the UPS, situation is repeating cyclically on the unit A101.
Please help us in determining of possible causes of error: either fault of module A102 or fault in inverter power circuit. Or something else ...
Reserve module A102 is absent, so we can't replace the faulted one.
See pictures of LEDs states and display symbols in attachment:
http://www.filedropper.com/upspics
Thanks. Any your help will be appreciated.
Best regards, Oleksandr Husyev.
There's a maximum lifespan for each and everything. And after 22 years your UPS has lived a long and full life. I think it is time to let it rest in peace and replace it with something new. Sorry I have to bring you this sad news.
Thank you for interesting.
Yes, we have checked it. The batteries are alive. They are charging without problems via UPS. But when we perform the UPS step-by-step switch up procedure, we receive an error on step when inverter is checking.
Hello everyone, I've been doing projects with Siemens and Rockwell PLC's for a couple of years now, and some softwares really helped me alot in...
2,646
Hello PLCs.net! Does anyone know how to configure S7 automated backups for S7 PLCs V15.1? I am having trouble setting up the ConfigurationFile...
1,187
Hi all, I understand that it's possible to backup a Siemens Simatic touch-panel using ProSave. However, from what I can tell there is no way to...
1,865
Hi all and Happy New Year. *I have a a Siemens S7-314 CPU and a number of I/O modules. *Powering the PLC is a PS307 120/230V (10A) PSU. *As a fail...
1,914
Hi guys, I've raised my problem on siemens forum ,but it looks that no one couldn't answer . Basicaly ,what I want to know is if the sketch...
2,515