Dear Experts:beerchug:,
I am new to Siemens WinCC:confused::confused:. I have created one Internal Tag 100_XV_01 (Unsigned 32-Bit), All I want to do is, If I check the Checkbox it should Set Bit 0 of the Tag and If i uncheck the checkbox it should Reset Bit 0. Same thing I would like to do with the Push button linked with PLC Tag. Please help me out to solve this issue.
I will be grateful for your kind guidance on the mentioned subject.
Thank you sir for you response.
Switch button is not there in WInCC 7.2. There is only Button (Momentary)we can make it switch by activating the Latch Down Property. But In this case how to Link a Tag 100_XV_01 (Unsigned 32-Bit) to set and Reset the Bit 0 for Press and Release of PB respectively???
You need two functions to achieve what you want GetPropWord and SetTagDWord.
GetPropWord reads properties (word value) of objects.
Place your script in miscellaneous>Object change of your check box.
First you need to know if your check box is checked or not.
You can do it like this
Code:
selected  = GetPropWord(lpszPictureName, lpszObjectName, "Process");
selected is word type variable.
If selected = 1 check box is checked, if selected = 0 it is not checked.
Basically:
Code:
if(selected == 1)
//set bit in tag
else
reset bit in tag
Now when you know when to set and reset bit in your tag you need to do it.
To set bit you need:
tag_val=GetTagDWordWait(TAG); //TAG is your unsigned 32bit tag
temp=tag_val|1; //OR your tag with 1 to set first bit
SetTagDWordWait(TAG, temp); wright new value to tag
To reset bit you need:
temp=tag_val&0xFFFE; //AND your tag with 32bit value where all bits ecxept 1st are set to 1 to reset first bit
tag_val and temp are DWORD type varialbles.
You can declare variables like this:
Code:
DWORD tag_val,temp;
WORD selected;
put these lines right before main code.
Put it all together and you'll have working script.
Thanks a bundle Mr. Moggie, Mr. Marcius and Mr. JesperMP for your kind assistance. I have tested the mentioned things and it worked, thanks a lot once again!!!
Hello colleagues, On a Siemens Multi panel (MP 377 12") of a machine (S7-300) at a customer's site, some parameters need to be changed that have...
305
I thought I was nearly finished on this TIA Portal/s7-1212C project (famous last words)... Up until now, I'd developed the PLC/HMI such that the...
1,558
Hi, I have a HMI which is a KTP1200 Basic. Let's suppose USER03 is logged in. How do I create a simple "Lock Screen" that appears if the screen...
677
Hi, At the moment, If the user fails to provide a valid username/password, the image attached appears "Invalid password or user name. Logon has...
1,577
Hello guys, Im using a siemens with WINCC in a computer and need to import to tag´s data fom a specific row in a SCV file, i have a working...
1,692