Hi all,

Does anyone know whether it is possible to Monitor/Program the PLC prog thru the OP3 to the S7-312. As in all connected and PC attached thru RS232 port on OP3??

:confused:
 
Is there anyway possible to communicate with PLC and have OP3 Online with PLC at same time??
 
Mylo said:
Is there anyway possible to communicate with PLC and have OP3 Online with PLC at same time??

If you use MPI as Seppo states then yes that is no problem to 'communicate' with the PLC and have the OP3 online.

Paul
 
Mylo,

you can NOT monitor the PLC program, nor program the PLC with an OP. You can only monitor and modify variables. Different interfaces do not change this.

Kind regards,
 
jvdcande said:
Mylo,

you can NOT monitor the PLC program, nor program the PLC with an OP. You can only monitor and modify variables. Different interfaces do not change this.

Kind regards,

Jean Pierre

Either I have mis-understood what Mylo was asking when he wrote "Is there anyway possible to communicate with PLC and have OP3 Online with PLC at same time??" or you have, you are correct in stating that you can not monitor a PLC program with an OP (or program a PLC), and I am certainly not disputing that.

I have interpereted Mylo's second question as asking whether he can have the PLC connected to the OP (via MPI) and have his PC go online with the PLC also via MPI at the same time, in which case the answer is yes.

Maybe I have now mis-understood what you have wrote, in which case I apologise for the mistake.

Paul
 
Hi Mylo.

The answer is yes. You can conetting with your PLC by normal way, any problem if you have another PLC or OP in the same MPI net, only you need to indicate How PLC you like to conect, is meand the address MPI of PLC that you need. :p
 
Paul,

as I see it you can interpret the question from Mylo in three different ways:
  1. Can I monitor/change the PLC program with the OP3.

    This is impossible as I answered.
  2. Can I connect to the PLC if my PC is connected to the OP and the OP to the PLC?

    This I don't know. I am almost sure it is impossible with an OP3 because this is one of the smallest OP's available. If it is possible at all, it should be with one of the larger (more expensive) OP's, maybe even only with the Windows CE OP's.
  3. Can I monitor/change the PLC program if I connect my PC to the OP and the PLC by means of one MPI network.

    This is surely possible. I did it on various occasions, but with S7-314 and TP170 or OP15.

    [/list=1]
    I did understand the question as being version 1, so I gave that answer. I think this table is now complete. If not I welcome everybody to complete it.

    Kind regards.
 

Similar Topics

Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
176
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
312
How can I integrate my S7-300 Simatic with the IFM AS-i Master AC1335 and its slave IOs, such as 2411 and Airbox 2041, into Simatic Manager?
Replies
0
Views
124
Hello.We are trying to convert a program written with S7-300 Simatic Manager to S7-1200 V16.Unfortunately, there is only LAD,FBD option in S7-1200...
Replies
2
Views
767
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,078
Back
Top Bottom