SIMATIC S7- 400H High-availability CPUs

YASS

Member
Join Date
Mar 2014
Location
Paris
Posts
3
Hi,

I'm involved with a project using Siemens S7 400 CPUs. Both CPUs are redundant (CPU1: StandBy, CPU2: Master) , i would like to download a new logic program. Could you please confirm to me the following way to proceed:

1. put in stop the stand by cpu (CPU1)
2. download
3. put it in Run
4. put in stop the Master Cpu (CPU2) ==> (CPU1 became the Master)
5. download
6. put it in Run (CPU2 became the StandBy)

Regards
YASS
 
Hi,

You don't need to do it manually. Step 7 or PCS 7 which you are using to configure and download will be taken care of this procedure. Just follow the instruction "pop-up".

Normally downloading logic should be able to do it CPU in Run and later they will sync or crossload it.
 
Thank you moez for your quick reply. However, i would like to download the new logic inside the memory card. i was requested to put in stop both CPUs then connecting to each CPU and download the new logic. Really i dont want to stop both CPUs. referring to your answer, i can download only in the Master CPU. right?
 
Hi Yass,

Here's what i did recently and it worked fine...

1. Power down system (Both CPUs)
2. Fit FLASH card to CPU 0
3. Wait until initialisation complete (STOP LED solid) (could be 10-15 mins sometimes!)
4. Highlight BLOCKS folder (left hand tree)
5. PLC > Download User Program To Memory Card. Wait until complete.
6. Power Down
7. Remove Memory Card from CPU 0 and fit to CPU 1
8. Fit second memory card to CPU 0
9. As Step 3

Hope this helps.

Regards,

Rob
 
Thank you Rob for your answer but i m really trying to avoid stopping both CPUs. I don't like to stop the running unit. knowing that i have the new program in my PC and i want to download it in both CPUs inside the memory cards.

Always thank you for your help.

YASS
 
Hi Yass,

Do you have access to a field PG or suitable card reader? Then you could use that to prepare the 2 x memory cards with the current working application instead.

Regards,

Rob
 

Similar Topics

We are facing intermittent issue with emergency stop and line stop. Line stop triggering with alarm of line stop push button activated at one...
Replies
10
Views
132
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
103
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
Replies
2
Views
181
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
Replies
7
Views
316
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
Replies
7
Views
329
Back
Top Bottom