mhans said:For 3 drivers all the U582 parameters are set to "2". I want to change this parameter to "1".
Siemens engineer said , he's not experienced about this parameter but it can be tried.
I want to try this.
What do you say ?
I say, the choice is yours, I am not going to tell you to do that. Changing this parameter tells the drive to display A030 as apposed to F030, you are obviously aware that the drive will keep running in this condition, this might cause you problems, it might not.
You can also turn off criterion 2 monitoring by changing U580 from 7 to 5, but only do this while you find the root cause of the fault.
The choice is yours.
Remember, these only MASK the fault not CURE it.
Paul