Single tank water level control using CJ1M CPU12
Download the program and then cross your fingers and then start the nuclear ractor :unsure:.
Need more info. help you.
Banker
The system work like this..
* Set a setpoint for the water level (eg. 200mm).
* Water is pump into the tank.
* The water flow into the tank controlled by flow control (Valtek Flowserve - 3400IQ Digital Positioner).
* The differential pressure sensor checking the water level.
* The flow adjusted to have the same level which set earlier.
* The flow will maintained when it achieved the level needed.
234
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
105
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
157
Hello, friends, I am trying to upgrade a system that uses an Onrom incremental encoder (E6B2-CWZ6C) connected to a Danfoss VFD (FC360), but now...
286
Hello, I am using Unity pro V15. I have Quantum CPU 671 and Ethernet NOE 77101 configured. I have configured IO scanning on NOE. I have attached...
189
