slc 5/01 cpu

roddbodd

Member
Join Date
Apr 2006
Location
alabama
Posts
15
a friend of mine gave me an allen bradley slc 500. when i applied power to it i got a cpu fault. i have tried 3 other cpu's and get the same fault. these units are supposed to be in new condition but have been on the shelf for some time. i have a 1747-uic interface. it will not communicate with the cpu. i am not that familiar with ab's. can anyone give me an idea of what's going on. thanks!
 
When you say it won't communicate, is it that you just can't see the PLC in RSLinx? If so then the driver is probably not set up correctly, which is the most common problem. Once you install the driver in your computer, and plugging in the cable, go to the Device Manager on your computer and see what comport it was assigned to. From RSLinx setup a RS-232 DF1 Devices driver make sure the comport that the computer assigned to the device is selected in the configuration window. Aslo in the COnfiguration window you need ot have the 1770-KF3/1747-KE device selected. Set your Error checking to CRC. I know that you definatly do not want to use the Auto Configuration. At this point click OK. All the rest of the defaults should be correct. You will then see the new driver listed. You can now close the Configure Drivers window. In the RSWho Window with the cable connected to the PLC and the computer, click on the new driver that you created and the PLC should show up. You can now access the PLC from RSLogix 500 or what ever software you might be using.
 
A fault would also occur if the CPU was trying to run a program that had a I/O configuration that didn't match the rack its now plugged into. Once you get the UIC communicating, you'll be able to download your program with the correct I/O configuration and the fault will clear by itself.
 

Similar Topics

I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
Replies
3
Views
527
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
Replies
7
Views
3,022
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
Replies
9
Views
1,808
I recently inherited some 5/04 CPUs and a single 5/02 CPU that I need to pull the programs from. The 5/04 CPUs didn't pose any problems. I...
Replies
14
Views
3,057
Hello, first of all, I want to say thanks to everyone who is seeing this post. I have a problem with an SLC 500 5/05 processor. I need to download...
Replies
4
Views
2,800
Back
Top Bottom