Quote
A "Stuck" Runtime error is detected on I/O module 3
Un-Quote
In a System comprising: SLC 5/01 CPU / 16 Input DC Sink / 8 Output Relay / Analogue Output, Modules (1 of each in that order)
We get the above fault, also noted:
Major Error Halt S:1/13 Flag=1, (all other flags=0)
This fault has been occuring on the PLC for the last 3 years about once every 2 month. We connect RSLogix, clear the fault. Then the machine is running again.
With regard to making a permanent repair can anyone advise the cause or where I should be looking?
thanks
micgent
No actually there is a better way to isolate what the real problem is
Get a copy of the SLC 500 instruction set look up the error corrections recommended under s:1/13 and s:6 the exact error can be recorded by following the instructions provided under the s:6 status bit it will provide a hex value depending on what error occured also I beleive s:20 and s:21 also provide some insite but check that under the s:6 heading in the instruction set. Also you can clear this with the keyswitch by toggling from program back to run or set s:1/8 to 1 clear major errors on power up
xx51​
A “stuck” runtime error is detected
on an I/O module.
If this is a discrete I/O module, this is
a noise problem. If this is a specialty
I/O module, refer to the applicable
user manual for the probable cause.
Cycle power to the system. If this
does not correct the problem, replace
the module.
this is from the instruction set I see now why Mickey recommended the surge suppression. I would look at the third card on the rack which I beleive you listed as an analog output module. Check the wiring make sure your not intermittantly tied to ground thru poor shielding. If the wiring is good then follow Mickey's suggestion
I am copying this questions from member E Nabors in the Practice Forum: http://www.plctalk.net/qanda/showthread.php?t=81258 SLC 500 error: "a...
2,092
I have a SLC 500 that looses the program sporadically when powered up. Yesterday we actually were able to retrieve an error from the processor " a...
2,787
I have a SLC 5/02 PLC in my office that I use to play around with (beginner)I have been useing this PLC for some time, Im using the 1747-UIC...
7,906
I have done some searching and found the cause of this error (1F51h) A loss of communications with one of the I/O cards caused by either the...
4,231
I have an strange thing happening with a SLC 5/04 On a 1746-OA16 output card I get 120 volts with or with out the output being true. The LED for...
1,853