i have one slc cpu and with the slot of 1747-SN scanner module. and it is connected in to 2 slaves by 1747 ASB modules with connected 6 input and 4 output discrete modules... this is running fine.
now, i want to add 1 input and 1 output modules in one of the ASB module
but, i don't know how it is communicating and working ..i also reffered 1747 ASB and SN manuales .and they are programmed using BTR/BTW Instructions
please any one simply said for this solution
thanks advance
If they're not analog input/output modules or any other specialty module, they won't need block transfers. You may need to change SW3-8 on the ASB to get it to recognize the new IO in your rack.
Are you adding the new modules to an existing chassis or are you adding a new chassis. Of course that would require an additional 1747-ASB module as well.
One of the tricky settings on the ASB module is that you must specify how many I/O groups the ASB module will require. Adding two modules may require that you increase the number of I/O groups. This would also require a (program) change for the 1747-SN module to tell it the rack size for that ASB.
This gets tricky because you will need to know the addressing mode (1-slot, 2-slot, or 1/2-slot). This is configured by the dip switch settings on the ASB module.
If you have trouble with these changes, let us know, and please include details such as the size of the chassis and the dip switch settings for the ASB module. If you have two ASB modules, please include those same settings for the other one as well. Even though it is a separate chassis, we don't want to cause a conflict.
OG
Good Morning , I have a SLC 500 rack with a 1747-L542 CPU and 2 DeviceNet scanner cards. I am having a terrible time going online with this...
4,385
Just Getting Started. I Have A Problem and Nowhere To Go. I Have a SLC 5/02 CPU With The 1747-UIC Hook Up (New Lap Top USB Port) I Can Config the...
4,610
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
535
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,028
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,821