Hello,
I was wondering if there is a way to view all the previous faults
from a SLC 5/05 controller?
Are there faults stored somewhere?
I was wanting to go back & look at all the faults that the controller
had faulted on if possible?
thanks,
No, there is no history of faults.
You might be able to send a message (MSG) to another PLC or other device on the network. You would have to write the code to do this in a "Fault Routine".
There's little point in storing faults internally, since quite a few of the major faults will clear the processor memory anyway, to protect itself.
I dont think so I once took an advanced class from RA and we did it with another node... the last scan of the faulted CPU sent the error code to a healthy CPU, if you are having a issue with one CPU that is losing everything (including comms) then you can set up another node to capture the error code
I don't think that will be reliable - you would have to read it very rapidly, even then there'd be a chance you can miss it before the memory is cleared.
I'm convinced the only way is to try and send the error code in a fault routine, which will get executed before the processor shuts down. Even then, some major faults, the non-recoverable ones, don't execute the fault routine at all
There is no "last scan" of a faulted CPU - it will exit wherever it is, execute the fault routine if one exists and it's a recoverable fault, the the processor will "fault".
We are talking about the same thing... just different terminology, a fault routine is what I was referring to, I dont teach Allen Bradley so my wording is not the same as your ;)
The advanced class that I took was about 15 years ago...
"last scan" = fault routine
It's good we got that cleared up.
But I don't think the OP has any chance of capturing the worst type of faults, i.e. those that don't execute the fault routine, and clear the memory.
I can't see justification in trying to capture just some of the faults, my efforts would be in ensuring the faults don't happen in the first place.
If a processor can be reloaded/restarted, then it unlikely to be a hardware fault, it's probably a software fault, and I would hunt them down...
Yes it does seem like a lot of work to capture faults... I dont think I have had that many to ever justify it, I did have a power supply that was giving me issues on a 5/04 a long time ago at that time I did the WAG and got lucky when I change the power supply it never came back 🍻
Howdy everyone, My company has a few machines running on SLC500 based PLC, and everytime it makes a part we count up on the counter which gets...
341
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
1,271
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
857
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,465
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
613