SLC5/03 comms problems
Rich19
Jul 2013
yorkshire
Hi I'm trying to communicate with an SLC5/03 with a 1747-CP3 SER A RS232 cable. Even moved the jumper inside the module from protect to program but with no luck. anyone had the same problem ?
Move that jumper back to protect. Its for firmware loading.
What driver are you using in RSLinx? Are you using a USB to serial adapter? What comm port is it using?
The serial port on your SLC5/03 can be configured for DF1 ( default) DH485 or ASCII protocol, do you know how it is configured?
Do you have the offline file? If so take a look at how the port is configured.
If you can post the file here and someone can help you look. Zip the file first.
Hi Mickey,
The Plc is on a working mc that seems to have a fault so no offline file. I am using AB-DF1-1 driver on comm 1 with 1747-CP3 cable. I'll move the jumper back aswell.
What happens when you click "Autoconfigure" in RSLinx?
Is/was there any thing connected to the serial port?
Are you using a USB to serial adapter? If so what comm port is the adapter taking?
Make sure you configure RSLinx for the same comm port.
Hi Mickey,
Managed to get hold of a 1747-UIC adapter and using driver AB_UIC DH485 on comm7 i was able to get straight online swapped an output to get the m/c back up and running.
Many thanks for the advice.
Hi Mickey,
Thanks for the feedback. Using the 1747-UIC means the serial port is configured for DH485 protocol. ( if you connected it to the SLC's serial port)
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
928
I have an existing machine with a SLC5/04 processor. It communicates to a Mettler Toledo IND780 scale controller via remote I/O and a 1747-SN...
2,055
Hi all I have 2 SLC5/04 plcs and a scada connected on DH+. I need to add a HMI which only has DH485 of DF1 available, I can connect to the DF1...
1,341
I need some confirmation from you guys about something I am looking into. I have a SLC5/04 and Reliance GV3000 drive. From what electricians have...
3,012
I have 2 sister machines (builder from Germany closed years ago) that each has a SLC 5/04 and a Panelview 550 with a serial cable between them...
2,236