SLC5/03 NIO4V Question
Maxkling
Mar 2011
Atlanta
511
I have a AB 5/03 and would like to use a 1749-NIO4V card to control some SSR's to power heating elements. I currently have thermocouples hooked up to Auber PID's. I know I cannot use thermocouples with the card usless I use a tempeture transmitter.
My question is would it be possible to use a thermistor and how accuratly would I be able to scale? Im looking to hold a set tempeture at 170F and 150-155F.
You need to investigate very closely the fact that ssr's have one phase hot all the time and that you might have voltage feedback through the backplane which will cause you problems. A co-worker had problems in the past, but i didn't know how he wired the system.
i had ssr's on a 100 kw heater that kept blowing and eventually replaced the controller with a mercyry contactor and temp controller.
regards,
james
You can't connect a thermistor to that card without a transmitter either. And expect an accurate reading.
Yes, I know about the thermocouple compatible card, but it is out of my price range for personal use. Thus, is why I'm looking for a way to make what I have work. This is a whole new learning curve as I've never temperature controlled with a PLC before. Ive only used the stand alone PID's and was just looking to learn more with using my rack instead of the PID's.
Has anyone used a tempeture transmitter to use the mV scale of the thermocouple to output a 10V scale for the analog card?
What you're looking for there would be called a Signal Conditioner. As far as I'm concerned, Action Instruments is the best in the business for that kind of product...
Something like this would work quite well for you.
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,577
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
1,294
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
653
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
940
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
991