SLC5/04 BTR/BTW Error code -9
PAC_Inc
Jan 2016
Va
I am working in a project that will use an AB Panelview 900 connected to a AB SLC5/04 using a 1747-SN Module on DHRIO. I have the digital portion of it working, but am having trouble with the Block Transfer within the plc program when I test the units. When I activate the BTR instruction to read a numeric data input object from the Panelview, the BTR instruction display's a -9 error code..
I am monitoring the BTR EN, BTR Start, BTR Enable-Waiting bits and they are coming on.. I then get a Er bit (bit 12) .. I have checked all setting that I am aware of and I can not find the problem.. Is this a set-up problem or what?
Welcome to the Forum !
Error code -9 is an ordinary timeout.
Do you have the discrete I/O working correctly between the PanelView and the 1747-SN ? You have to at least verify that the RIO protocol is up and running and you've got green LEDs all around.
Block Transfers really only have two properties when they go across the wire; their Direction and their Length. So it's crucial in PanelBuilder32 to have defined the proper Block Transfer type (Read or Write) and the proper Length.
If the Length defined in PanelBuilder doesn't match the Length in the BTR instruction, the instruction will fail.
It would help if you could post the programs of both the SLC and you PV.
Also tell the forum which data object you are trying to read. (address)
Okay, Got it to work... I had the wrong number in the BTR/BTR in the instruction box.. My 1747-SN resides in Slot 1 so, I had that for the M0,M1 file setup, ie Mo:1.600 and M1:1.700. When I did the slot number above it, I also used 1 for the slot... Wouldn't work.. Changed the value to 0, then it worked...
Everything is transferring perfect.. I then set it up as a Bi-direction Alternating Repeating aand still good to go...
Ken, you are right on the different valve in the Block transfer of say 10 words in the Panelview setup, then using a different value say 5 for the BTR/BTW in the SLC program... Won't communicate ... Put it back where both devices are using the same number of words and it works perfect...
I was using the panelview to transfer Integer (N) valves to the SLC for changing Timer preset values.
Tthanks for the help...
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,562
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
1,278
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
640
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
930
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
984