SM2 add module to Compact Logix
Oct 2015
Melbourne
23
Hi all,
I have a L24ER, working fine. Want to add a 1769-SM2 module. Installed, no worries, go online and can see it on the 1769 bus when I do a "module discover", however I cannot create it in the project until a "Profile is added" for the module.
The module does not show up on my available list of modules.
I can reflash the module with the control flash package/system.
From what I can tell, I need to import the AOP for this device. Try as I may, I cannot find it anywhere on Rockwell's site, only the reflashing app.
Anybody got any advice or experience here?
Thanks,
Graeme.
Thanks Ken,
I will follow this method.
Quickly looking at it, all seems to lend itself to VSD drive connections. I have purchased this module hoping to connect to generic modbus devices, similar to what you would do on channel 0 as RTU master on a MicroLogix 1400
Good luck
Thanks Ken,
Yes, this module does, indeed, connect to and allow for Modbus comms.
But, prepare for a long haul of manual reading and frustration.
The 1769-SM2 was built to connect CompactLogix and MicroLogix 1500 systems to A-B component-series drives, which use an RS485 network called "DSI" for "Drive Serial Interface", which is a superset of Modbus RTU.
The module can also communicate with general-purpose RS-485 Modbus RTU devices, but as noted it's a little more difficult to do so.
But that's what you've got now, so crack open the user manual and the end device manual and commence to engineering.
After battling this one for a few weeks, my primary recommendation is to carefully consider ELECTRICAL ISOLATION of your Modbus network, even though the books might not specifically recommend it.
Hi Project's PLC is a 1769-L36ERM used with a Siemens LME73 Flame controller. I have to establish communication between these devices thru a...
1,599
So I have a system that is running on DeviceNet. We have been having nothing but problems with it for the last 3 years. I am trying to switch...
1,286
Hello everyone I am trying to improve my skills but am having some problems, I hope someone can help. I am using an AB micro 1500 LRP C and a...
2,454
Hello everyone. I'm trying to communicate a Controllogix L36ERM with a 1769-SM2 Modbus module to a Schneider-electric Altivar 312 Modbus motor...
2,494
Hi All. I have a project running 3 x MODBUS channels out of a SM2 module configured as a RTU Master. There are two MODBUS slaves on each channel...
1,296