Smoothing Analog Inputs
WuShockKS
Mar 2021
Kansas
Hello, I'm pretty new to RSLogix 500. I'm trying to smooth out the raw analog input. Current 4-20ma. I'm in an environment that I can not control the noise. The transducer is bouncing and throwing off the SCP instruction.
1766-BWA PLC
W/1762 IF2OF2 Analog card
I don't see a filter option in the hardware configurator, unless it requires to be online (just mocked up a controller and card in logix 500, no real hardware to test against). Probably will have to make your own averaging instructions. I would look more closely into controlling the noise however, there is likely a way to eliminate the noise. 4-20mA should be reasonably immune to noise anyway, being DC. Grounding and shielding is done correctly?
Most on-card filters are geared to reducing 60/50 Hz noise. I have had good luck using the digital filtering technique attached. I usually make the time interval between calculations and the number of steps operator adjustable.
Mickey has posted a formula for doing this that a lot of people seem to make use of. Could somebody please give a simple "Ladder" diagram as to...
22
12,278
Hello, I am using a P1000 CPU (P1-540) with a P1-04DAL-2 and a P1-04ADL-2 I tried doing a data transfer now I am trying to scale them both...
1,111
Good Morning, So i have attached some really crude programming to try and work around my inability to smooth an anlog signal (actually several)...
22
8,601
I am trying to make an input less jumpy. The monitored input has large spikes, and changes too fast. I am trying to smooth it out. I am using...
2,144
Good morning guys, So i know this is extremely basic, but im just starting our with analog signals and trying to wrap my head around it. I...
4,347