stuck runtime error
Markn902
Apr 2016
Indiana
25
Hi everyone again ��. I am having a problem rack that has been giving me fits.This time it has a fault that says.
a "stuck" runtime error is detected on an IO module exact slot cannot be determined. Any thoughts? Thanks in advance
I apologize I am working with an SLC 500
1747-L524.8 slots w/ CPU being zero. 16 I/O modules.
This one can be tough to nail down. Basically you have one (or possibly more than one) card that is so fubar, that it has the backplane so jacked up the SLC can't even tell where the garbage originates.
Get your spare cards for each type in use and swap them one at a time until the symptoms change.
Another potential problem is ground current noise but most likely there will be a faulty card or a serious load problem on a relay card.
Relay cards should be your first suspects, and even without spares you can remove the wiring arms from them and see if the problem clears. 1746-OW16 cards have a couple of relays that are near enough to the backplane that a failed or failing inductive load connected to one of those relays can induce a current onto the backplane that will screw things up for the whole rack.
Another thing to try is the rack power supply. If you have a new spare power supply, it is easy enough to change that out too.
I am copying this questions from member E Nabors in the Practice Forum: http://www.plctalk.net/qanda/showthread.php?t=81258 SLC 500 error: "a...
2,092
I have a SLC 500 that looses the program sporadically when powered up. Yesterday we actually were able to retrieve an error from the processor " a...
2,787
Quote A "Stuck" Runtime error is detected on I/O module 3 Un-Quote In a System comprising: SLC 5/01 CPU / 16 Input DC Sink / 8 Output Relay /...
4,632
I have a SLC 5/02 PLC in my office that I use to play around with (beginner)I have been useing this PLC for some time, Im using the 1747-UIC...
7,906
Hi All, I have had a "stuck" runtime error come up on a 5/05. It has happened a few times. Exact fault code is 1F51h. This originally happened a...
4,707