Just purchased Studio5000 and have it installed, will be connecting to 3 brand new Powerflex 7000 VFDs. In setting up the module, how can I tell if I need to use MV Drive via 20-comm-er or MV Drive, Fourth Gen Control via 20-comm-er? The ethernet module is a 20-comm-er. The drives are not powered up yet and the contractor will not allow me to power these up with external 120v testing circuit. I'm trying to get a jump on the CompactLogix programming to not delay the startup of the new VFDs.
It should be a fourth gen as they have not made Classic's for some time now.
If they have PanelView Plus displays, then it will be a Forge drive which are fourth gen drives.
The 20-COMM-ER has 2 ports to allow for daisy chaining units together and DLR.
PF6000's are a completely different drive, the PF7000 is fully designed by Rockwell, whereas the PF6000 is a design they got from a company that they bought out in China.
The PF7000 drives are a current source drive, the PF6000 are a voltage source drive and use multiple modules to achieve their output voltage, they also use a transformer on the input.
The PF7000 drive does not use a transformer as it runs at the input voltage, the ones I commissioned were either 3300v or 6600v (but they come in different voltages for different countries), the only PF6000 that I commissioned was 415v input and 3300v output.
I have two of the same PCs and one can connect to my drives through the studio 5000 v34 program and the other PC can not gets the Error posted in...
959
Recently started working a side job at a recycling plant and have been asked to go through some of the drives that the operators are currently...
19
4,878
I have an array of 55 REAL values. Is there a way to multiply based on the array location ? I have 55 transfer belts that are equally spaced...
154
Hi Hope you all are doing well. Iam working on a project with some AOI. I also hate no online edits... lol. My problem occurs when I use a UDT...
163
I am not sure if this is possible but if there is a way, you guys would be the ones to know. I am currently working on a project where we are...
226