Before you waste ANY more time on this idea, you have to understand one core basic concept about what you are thinking of doing here.
100HP at 230V single phase is going to require over 420A of 230V single phase current! You cannot get around that fact, and in fact because of losses in the VFD and transformer to go from 230-460V, you will actually more likely start approaching 500A of 230V 1 phase current. Unless your customer has some sort of extremely unusual service from the utility, I seriously doubt he has anything larger than a 400A service, which in reality is actually going to be limited to 320A (because that's the limit on meters).
I have another customer in a similar circumstance that has a 1200A 230V 1Ph service
Usually power companies are happy to assist in supplying 3 phase (or bringing 2 of the 3 phases for an open delta) when you are trying to install such large motor load. Starting a 200HP+ motor on a 230V single phase line can defiantly blink lights on that line, and after enough calls to the public service commission, they are happy to assist.
I need small power supply that has very small ripple and 250VDC for my workshop. I came to idea to use DC bus from VFD that has 3x230VAC output as...
2,098
Currently we are supplying a couple of hundred 753's with an input voltage of 435-440 VAC. Our utility company is going to correct this next...
1,370
hi all manoj here . I need help .. i have one application i want to run compressor it's supply voltage is 120v ac/ 60 Hz. can i convert this...
3,807
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
204
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
21
583