Sync of Two Generator (80kW KOHLER) Using Plc
Sourav Sau
Oct 2017
India
I want syn of two same 80 kw generators (Gen Model--KOHLER 80EFOZDJ) using PLC. The gen is electronics engine controlled by ECU (level 14, Deere & Company). Not understood what type of load and Speed sharing unit is required. I need a controller which will check all synchronous condition and if ok then a signal to the plc. Need to adjust the freq by adjusting the rpm autometically. So please suggest for a solution.
Woodward easYgen is best - you will have to adjust speed and voltage from the easYgen - load sharing. Make sure the Kohler can accept a bias signal for both. They are toys really and it may not be possible. Working on a job set up with easYgens at the moment - 4 x 730kva sets - 11Kv.
First of all thank you for your valuable reply..
I got this message from the generator supplier.... Pasted below..
“Generators are ready for synchronization. I understand that you are going to use a 3rd party switchgear for this purpose.
In this case we just need 0,5 -4,5VDC input speed signal from the external paralleling controller to each generator.
You must use SBP (Speed bias positive) and SBN (Speed Bias negative) that you can find inside the controller box of each genset.
Droop settings will be handled by the programming-setting of the external controller you intend to use.”
So please suggest further..
Check the easYgen controllers manuals - they do positive negative biasing.
hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
54
I have to start out by saying I am not a PLC programmer and I have basic programming skills but mainly use software as a troubleshooting tool. I...
134
Hi currently my existing PLC using AB motor & driver to spin production, however customer want to another set, if this possible we use different...
224
Hello, I am trying to create an AOI that will retrive the clock datetime bits from a master plc through a generic message read instruction and...
499
I have a problem with time sync working in this topology. I have a plc with grandmaster clock controlling motion groups. I wanted to add kinetix...
1,050