System Startup Seq
asterof
May 2007
Califonia
554
Contrologix L73
Running a new Ammonia/Glycol Refrigeration system
we have
Compressor Control
Condenser Control
Chiller/Glycol Pump Control
Plate & Frame HX Control
So in what order would you start these systems
I do have a refrigeration background, so here is how I would do it.
Start condensor system. Start compressors. Once desired psi or vacuum is acheived, start the pump and HX control. You didn't mention evaporators, but they should turn on when the pump turns on. If there are a lot of evaporators in the system, I would stage them on one or two at a time so as not to place a lot of demand on the system all at once. Every system is a little different and has it's own 'personality'. If this is a new system, there will need to be a lot of babysitting and tweaking to figure out what is best for your application. Good luck!
Hello, I am trying to have an RSView ME Station File (.mer V10) run on MiniX PC attached to a touchscreen monitor. PC has been configured to...
785
I get this error on startup and I can't even uninstall the software to reinstall. Any suggestions?
14,507
There is another problem facing me, i have to develop a project in RSVIEW32 but when i open RSview32 runtime, its open in small window if i run...
7,736
Hello, I have no training in maintaining potable water systems, so forgive me if some of my terminology is far off the mark or if I'm focusing on...
96
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
96