TCP communication with S7-1200
Weo
Feb 2006
Sweden
82
Hello
I want to add a new Tcp connection to an existing project.
Cpu is a 1214 and today there are only one configured connection, that's a HMI connection.
However, when I try to add a new connection in the network view, I only get the choice to add a HMI or a S7 connection. Tcp is not in the drop down menu (like it's when looking in a 300 or 1500 project for example)
As seen in attached screenshot there should be 8 reserved resources for open user communication.
CPU limitation with regards to TCP connections?
Anyone came across this before?
Added: I want to use the onboard Profinet port for the new Tcp connection.
you don't need to configure the TCP connection in the network view, like you would have done this for the S7-300/400.
You define the connection endpoint (IP address, port number) and the type (TCP/UDP/Iso-On-TCP) in the parameters for the T-blocks. (TCON, TSEND, ...).
Hi
But is it not possible to make a configured connection in S7-1200 series, that requires less code?
You suggest a programmed connection, then I have to use The TCON and TDISCON to establish The connection?
Is that my only option?
After reading some more, conclusion is that in the 1200 series you MUST establish the connection with the TCON. In previous project with a 1500 serie CPU I configured a connection, that is not an option with the 1200 serie.
Also found out, so looks like a good improvement to me.
No extra programming, instead you get everything about the connection collected in your program block.
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
397
Dear Experts, Warm Greetings ! By using TCON,TSEND,TRCV,TDISCON block,I am trying to make communication with my...
1,497
Hi friends, This is my first work with simatic and I am having some difficulties to comunicate S7 with HMI. HMI: T5F-2 Beijer Electronics S7...
3,566
Hi to all, I am using s71200 plc... I am sending some spec values from my plc to the module1 continuously through TCP communication.... Now...
3,462
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
213