Yes, I understand the END rung.

I did not know the significance of file 2. I usually put it at the end of the file that has the most math functions and this time I put it in the last file. Today I linked up a counter to it to see how many times it was latching, just before the UTL.

I'll move it all to file 2.

Thank you,

OK, a quick lesson...

The processor will only execute file 2 automatically. (there are other files it will execute automatically, but more about these later).

User code that is placed in other files 3-255, is executed (usually) by the use of JSR (Jump to SubRoutine) instructions. After a Subroutine is finished, code execution always resumes at the calling routine.

Subroutines can "call" other subroutines, (we call it "nesting"), but each subroutine resumes from where it was "called"... This means that the "END" rung in file 2 will always be the last rung scanned in the "scan cycle".

Exceptions to the above...

STI (Selectable Timed Interrupt) : A ladder file that can be configured to be executed at a fixed time interval. The code is executed periodically, interrupting the main "scan cycle".

DII (Digital Input Interrupt) : A ladder file that can be configured to execute when a specified Input bit becomes true. The code is executed only once for each False to True transition of the specified input.

Fault Routine : A ladder file that can be configured to execute when a major fault is detected. The fault routine may, at the programmers discretion, clear the major fault, and allow the PLC to continue, otherwise the processor will halt, stop, red-light.

Hope this helps your understanding....
 

Similar Topics

Hi all, & a happy New Year. it's been a long long time since on the site, & true to form I need your help once again. I have been tasked with...
Replies
13
Views
2,780
Hello everyone! I have a task to measure the temperature outside and inside of a building, and compare them. I am working with the xcp pro, and...
Replies
3
Views
2,158
I was wondering if anyone has ever had to setup a system to monitor temperature of the contents of a parked stationary railroad tank car. I can...
Replies
6
Views
2,556
I am looking at monitoring the temperature inside a PLC enclosure to feed back into an HMI, but I haven't used thermocouples/Pt100 before...
Replies
4
Views
2,582
Dear All, I'v 1 project which is monitoring 100 channels of thermocouple's temperature by PANASONIC PLC. Any suggestion for this project ? which...
Replies
0
Views
2,939
Back
Top Bottom