The tags of I/O point
Shawn
Oct 2003
24
Hi buddies,
As far as I know, Controllogix 5550 doesn't use I/O points' address as a SLC PLC, it uses tags for all Timers, Counter, Relays, and I/O point.
The problems is, How I can find a Tag for a unused Input point so that I can use it.
Thanks.
Each card in the I/O tree is given a name. From that name each I/O point is the name with the I/O extension, example(name.0). Individual tagnames can alias each I/O point name. If the tag is for a direct I/O point there will also be an alias listed for that point. If you sort by alias you will see if there are any additional I/O points available, or not used because they will not be listed.
Hi Buddy,
Thanks for you reply. Do as you told me, I can find the tags for the module. But the new problem is, why they setup 3 tags for each module.
As example, module(7):1756-OB16E LocalOutput07
Module Defined Tags
|___Local:7:C
|___Local:7:I
|___Local:7:O
Thanks again.
An Output Card has a
C for card Configuration and Status
O for the Outputs
I for Simulating Outputs - I have not played with these at all, so I am not positive of this.
An Input Card only has
I for Inputs
Some cards, like a DNB (DeviceNet Scanner), will also have a S for Status.
Hope this helps.
Hello, I have a FactoryTalk Historian where I've configured some tags to record a couple of signals. This bit works as I check the historical...
1,724
Is there a way to import tags form RS5K to C-more database that are aliased to AB Point I/O. When I import tags all tags associated with the Point...
3,190
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
46
Afternoon all, I'm working on setting up a large excel recipe table for porting updates through the Linx Gateway RTD/DDE function into my recipe...
127
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
91