TIA remote access S7-1200+KTP600

AlecTek

Member
Join Date
Sep 2010
Location
Vancouver
Posts
155
Hello everyone,

I have a system of S7-1200 + KTP600 + router. The questions are which ports needed to be forwarded, are the followings correct?

ip of S7-1200 ***.***.***.1
ip of KTP600 ***.***.***.2


Ports to forward to S7-1200: 102
Ports to forward to KTP600: 2308, 50523, 5800, 5900

-----------------------------------------------------------------

Another question: I think I missed put the startup mode to run, the PLC S7-1200 stopped after a power failure. Is there any way I can start it locally without remotely connecting the PLC?

Thanks!
 
Alec,
Not sure about which ports to forward for the HMI, but regarding the startup mode for the 1200, you have to connect with TIA to change the mode. To fix it, change the properties in the HW config and redownload the config.
 

Similar Topics

Hello PLC Friends, I'm starting my final year project with a given rig and I'm thinking about incorporating a remote access feature where I can...
Replies
2
Views
377
Siemens S7/TIA v18: "Remote" updates/bug fixes to PLC code & HMI screens..... Hi, The PLC application I'm working on will soon be delivered to...
Replies
5
Views
600
Hi! I have a s7-1200 and a comfort panel connected to a **** cosy. I've been able to download to both devices for a while but now out of nowhere...
Replies
14
Views
7,096
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
108
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
197
Back
Top Bottom