I have siemens S5 plc and would like make a programme for gas flow totalizer following are the details
I have flow transmitter which outputs 4-20 mA
It has flow and totalizer mode i am getting 4-20 mA for flow and i am getting flow rate on my HMI now i would like to get it in totalizer reading over HMI
Please help
Greetings Rajesh,
Your Flowmeter sends you ( L \ min ) or ( L \ sec)
You need to know the mass that flows in a given period of time , You need a value in ( L )
So if your meter sends 4-20mA which represents:
A- L/sec:
Each sec you take the value and mutiply by one
B- L/min:
Each sec you take the value and mutiply by 60
And so on..
Now for the totalizer part:
Each second elapsed run this formula:
Total_mass = Total_mass + (flowmeter reading * 60)
assuming that it reads L / min.
This can be done with scripts which is avilable in most SCADA software packages.
Anyway, If I were you, I woudn't use my HMI for this job, I think it's not accurate (because of the delay in timing in PC hardware and software)
You can use the PLC to do the job and send the value the your HMI
EDIT: There are mistakes in my last post, sorry!
Flow rate (L/min) must be divided (not multplied) by 60
So the formula (Which is excuted every 1 sec) should be like this:
Total_mass = Total_mass + (flowmeter reading / 60)
Hi, So we have a flowmeter installed but doesnt have a feature to send a pulse to plc for it to compute the total volume. I want to somehow...
587
How is it going y'all? So We have had a pesky problem with an EH 300 flow meter. We are using EIP to reset the totalizer, and for some reason the...
801
Good morning, I have a flow meter that has an output pulse configured to 378.541 liters per pulse. My question is, do I just count the pulse per...
19
1,816
Good morning, I have a flow meter that that has an output with is a pulse. The pulse is configured to 378.541 liters per pulse. My question is...
708
Hello You guys helped me with a similar issue some time back on storing totalized values to different tags each month. I have a similar issue...
19
1,508