Transfer restrictions when using Siemens Moby I

Borte

Member
Join Date
Feb 2004
Location
Norway
Posts
238
Hello!

I wonder if someone here is familiar with the Simens Moby I (RFID)system?

I'm trying to write 50 bytes to an MDS403 (8Kb) memory tag over an ASM450 unit controlled from a 316DP2 CPU, but so far it only allowes me to transfer 30 bytes. As soon as I pass that limit it'll report the following error:

-> Input or output areas are too small for the telegram length used.
-> Read or write command with excessive length used
-> Adjust bus configuration of the master module.

I have used the same system with the same code to read / write 50 bytes of data before, the only difference was that I used a 413 CPU in that application.

Anyone have som toughts about this?

Regards
Borte
 

Similar Topics

I'm trying to verify a project with a PLC. The Transfer Setup menu item is grayed out and every time I click Verify with PLC, I get an error...
Replies
1
Views
64
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
Replies
0
Views
92
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
106
Hi all, Im having trouble transferring a program from one panelview 550 to an new one. I can insert a flash card into the old panelview and upload...
Replies
20
Views
362
Hi Everyone, I have a customer that needs a CQM1H (CPU51) replaced. They purchased the processor new-old-stock from a source they found online...
Replies
3
Views
357
Back
Top Bottom