Transfer
R.Mati
Nov 2010
Melbourne
25
Hi
I have a Tank (A) with a level sensor attached on the top.
Tank (A) calls for product from Tank(B)(ONLY) 100 Liters at a time.
I have no idea how to measure 100 Liters that needed to be transfered from (B) to (A).
Hope that it clear.
You could put a flow monitor and use that to measure 100 liters. You'll want to search the forums for "Totalizer"
Or, if the setup allows it, you could use the existing level sensor and the dimensions of tank A to find the volume of tank A to make sure it gets filled 100 liters. This would work only if A wasn't being emptied by some other source.
Or, the same for Tank B, again if tank B isn't being filled by another source while being emptied to fill A.
TANK (A) gets emptied by some other source
Simplified... a lot depends on what medium you're transferring, how and what other factors affect the levels.
Are we to assume that once the level switch requests a fill to Tank A, Tank B releases it's load?
Can Tank A still be emptying whilst Tank B is trying to put 100l into it?
Thanks for your reply,
The case is like that.
Tank (B) has a mix of Resin and some pigment when the mix is ready, Tank (A) would be ready to call for that mix from tank (B) and would call only for a 100 Liters at a time.
BTW, Tank (B) level is measured in mm
Tank (A) level is measured in L
and there is no flow meter on the pipe between A & B
all I have is a Pump and valve.
No, at this stage.
BUT they might ask for it I am pretty sure.
Depending on how accurate you want your 100 litres to be, I have some suggestions, ranked in order of cost/accuracy...
1. Use the existing level sensor on tank B to determine 100l has been taken from it. You would need a "Dip Table" of the tank to determine mm height versus volume. Doesn't allow B to be filled while transferring.
2. Use a PD pump run for a pre-determined time would give reasonable accuracy. Allows for B to be filling AND A to be emptying concurrently.
3. Use a flowmeter between B and A, for best accuracy. Also allows for B to be filling AND A to be emptying concurrently.
Either way would allow A to be emptied while B is transferring.
Can you always the run the VSD at same speed ? If so, you could work out the length of time that the Pump had to run to deliver 100 litres (at a pre-determined speed) you just run the pump for that length of time. Not very accurate but without extra instrumentation it may work.
I'm trying to verify a project with a PLC. The Transfer Setup menu item is grayed out and every time I click Verify with PLC, I get an error...
71
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
97
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
115
Hi all, Im having trouble transferring a program from one panelview 550 to an new one. I can insert a flash card into the old panelview and upload...
20
367
Hi Everyone, I have a customer that needs a CQM1H (CPU51) replaced. They purchased the processor new-old-stock from a source they found online...
360