Transformer primary side protection
monkeyhead
Sep 2004
I'm right here
656
I've got a machine that appears to have it's transformers protected completely wrong. They've got a 7.5 kVA, 480v to 240v/120v, single phase step down transformer protected on the primary side with a 35A breaker. One the secondary side they have 3 seperate circuits, a 30A center-tapped 120V circuit, and two 30A 240V circuits.
I've always used the following formula on transformers.
Primary side: 1.5 * (VA_Rating / Primary_Votage)
Secondary: 0.8 * (VA_Rating / Secondary_Voltage)
So for this transformer, I'd end up with 25A breakers on both sides.
The bizarre thing, is that they have an amp rating of 15.6A printed on the schematics next to the transformer, but still have a 35A breaker protecting it.
Then they also use a a much smaller 250VA 120V to 24V step down transformer with a 10A breaker on the primary and nothing on the secondary. So if this thing shorts out on the secondary, it seems to me it will burn itself up well before the circuit breaker pops.
Am I totally missing something, or have I just come across a design flaw? The OEM has hundreds of these machines deployed so this seems surprising to me.
From what I can tell from NEC Article 450.3, it looks like they are allowed 250% on the primary if they also have secondary protection, which can itself be rated up to 125% or rated. But unless they have an overall secondary breaker i think they are incorrectlyt sized on the secondary.
Without any other information I'm gussing that the 120/24 transformer is covered by Note 3 from table 450.3(B).
Keith
Thanks Keith. I knew my calculations were on the conservative side, but I didn't realize that when you have both primary and secondary protection that you can step up the primary side protection to 2.5 times the rating.
They do seem to be violating Note 2 of Table 450.3(B) on the secondary.
On the smaller 250 VA there's no manufacture provided thermal overload protection, so I think they just blew it. The primary really shouldn't have any more than a 3A breaker based on this table.
I also need to verify what's in the enclosure... I've found other problems on these schematics, and popped open the control panel to find that everything is actually done right. Maybe they've got a guardian angel wherever they're getting their panels built that's keeping them safe.
Folks, I am designing a control system for an industrial machine. Machine is 480VAC / 3PH powered. And I have a 480 / 120V transformer for control...
1,411
Hi all, I know this sounds like a dumb question, but.....I'm thinking out loud...and maybe I shouldn't do that.... Upcoming project involves...
4,165
Ignore - I asked this question already and found my answer.
1,032
Hi all Where can i find this transformer ? Pri 480 v 3x 0.12 A Sec 400 v 3x 0.12 A 3 phase Type DTS 80 50/60 Hz
3,579
Greetings experts, Can current transformers be used on the incoming mains (480, 3P) of a machine that has regenerative VFD's? Current...
3,239