agarb, you need a new DC drive. Discard the old one (send it to Liefmotif).
Your motor is a compound wound 40hp motor with 230V armature and unknown field voltage and current.
I would buy a 230V non-reversing, non-regenerative DC drive with an adjustable field regulator.
Before you dismantle the old drive, check the current in the F1 to F2 circuit. That is the shunt field and note the highest current you see among all of the different speed steps. It might change between steps and it might not but we are interested only in the highest current. Also, be sure to note the polarity between F1 and F2.
Buy and install the new drive being sure to preserve the connection between one of the A leads and one of the S leads. The remaining A and S leads are your armature connections to the new drive terminals labelled A1 and A2.
Connect the F leads to the corresponding terminals on the drive and set the field regulator for the lowest current or voltage. Power up the drive and slowly adjust the field regulator up until you have the same current and polarity flowing between F1 and F2 as you noted before for maximum current.
Energize the armature circuit and note motor shaft direction. If reverse, stop, power down, and reverse the connections on A1 and A2 on the drive. Do not change the F connections or the motor junction box connections.
This should give you a properly running motor with better torque at all speeds. If you find that you can't quite get to full speed, set your field regulator current down slightly until full speed is reached at full armature voltage.
Be very careful that the armature is not energized with no field current or very low field current or an overspeed run-away condition can occur. You will likely explode the armature if that happens and the motor will be ruined. There is significant personal hazard when this happens as well and we wouldn't want you to end up in the same state as the motor!
Good luck!
Your motor is a compound wound 40hp motor with 230V armature and unknown field voltage and current.
I would buy a 230V non-reversing, non-regenerative DC drive with an adjustable field regulator.
Before you dismantle the old drive, check the current in the F1 to F2 circuit. That is the shunt field and note the highest current you see among all of the different speed steps. It might change between steps and it might not but we are interested only in the highest current. Also, be sure to note the polarity between F1 and F2.
Buy and install the new drive being sure to preserve the connection between one of the A leads and one of the S leads. The remaining A and S leads are your armature connections to the new drive terminals labelled A1 and A2.
Connect the F leads to the corresponding terminals on the drive and set the field regulator for the lowest current or voltage. Power up the drive and slowly adjust the field regulator up until you have the same current and polarity flowing between F1 and F2 as you noted before for maximum current.
Energize the armature circuit and note motor shaft direction. If reverse, stop, power down, and reverse the connections on A1 and A2 on the drive. Do not change the F connections or the motor junction box connections.
This should give you a properly running motor with better torque at all speeds. If you find that you can't quite get to full speed, set your field regulator current down slightly until full speed is reached at full armature voltage.
Be very careful that the armature is not energized with no field current or very low field current or an overspeed run-away condition can occur. You will likely explode the armature if that happens and the motor will be ruined. There is significant personal hazard when this happens as well and we wouldn't want you to end up in the same state as the motor!
Good luck!